Tool Board Heater Tuning Leading To Faults
-
@fcwilt it included M307 commands that were generated from the autotuning and saved using M500
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@fcwilt it included M307 commands that were generated from the autotuning and saved using M500
So we can ignore the ones in your config.g file?
Frederick
-
@fcwilt They're identical
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@fcwilt They're identical
So you copied the lines from the config-override.g file and put them into your config.g file?
I assume you re-booted.
Frederick
-
@fcwilt Affirmative
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@fcwilt Affirmative
Strange problem you are having.
You posted a screen shot showing heaters Ex0, Ex1 and Ex3 faulted.
Were all three heating at the time?
Frederick
-
M308 S1 P"20.temp0" Y"thermistor" T100000 B4725 C7.06e-8 A"Ex0"
On T0 you use a thermistor but not with the other tools?
What is your tuning command. -
@fcwilt Yes, all 3 faulted (nearly) simultaneously, when heating is initiated simultaneously
-
@diy-o-sphere Changed to thermistor (actually changed hardware) just to try troubleshooting
-
@kevinmar
CAN addresses set correctly? -
@kevinmar did you see my comment about retuning with a silicone sock in place, and my suggestion to reduce the M307 R parameter?
-
@dc42 said in Tool Board Heater Tuning Leading To Faults:
If after re-tuning with the silicone sock on (if necessary) the heaters still fault, you can try reducing the M307 R parameter. Try a 30% reduction.
I added the sock, retuned, and it still faulted.
I reduced R from 2 to 1.5 and even to 1.0 and it didn't help
-
@diy-o-sphere lol yeah, boards working fine otherwise
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@dc42 said in Tool Board Heater Tuning Leading To Faults:
If after re-tuning with the silicone sock on (if necessary) the heaters still fault, you can try reducing the M307 R parameter. Try a 30% reduction.
I added the sock, retuned, and it still faulted.
I reduced R from 2 to 1.5 and it didn't help
Did the R value change much when you added the sock, or was it just the C values that changed?
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@fcwilt Yes, all 3 faulted (nearly) simultaneously, when heating is initiated simultaneously
If you execute a M570 command from the DWC Console what value does it report?
Frederick
-
@dc42 C values changed when tuning with the sock.
R values were a manual change
-
@fcwilt "Print will be terminated if a heater fault is not reset within 10 minutes"
-
@kevinmar confirm you are running firmware 3.3 on both main board and tool board?
-
@dc42 yes, 100%. All running 3.3 non beta or anything
-
@kevinmar said in Tool Board Heater Tuning Leading To Faults:
@fcwilt "Print will be terminated if a heater fault is not reset within 10 minutes"
As a test have you commented out the settings for all but one tool heater to see if that makes a difference?
Frederick