Resurrect.g problem
-
Resurrect prologue.g
M116 ; wait for temperatures
G28 ; home all towers
M83 ; relative extrusion
G1 E10 F600 ; undo the retraction that was done in the M911 power fail script
G4 S5
G1 Y50 F5000; Mi muovo per togliere il filo
G1 Y0 F5000
G1 Y50 F5000Actual resurrect.g
; File "0:/gcodes/bloccaggio-a-pressione-definitivo-v2.gcode" resume print after power failure at 2021-04-13 14:34
G21
M141 P0 S40.0
G29 S1
T-1 P0
G92 X128.952 Y115.714 Z0.650
G60 S1
G10 P1 S23 R0
G10 P0 S240 R240
T0 P0
M98 P"resurrect-prologue.g"
M116
M290 X0.000 Y0.000 Z0.000 R0
T-1 P0
T0 P6
; Workplace coordinates
G10 L2 P1 X0.00 Y0.00 Z0.00
G10 L2 P2 X0.00 Y0.00 Z0.00
G10 L2 P3 X0.00 Y0.00 Z0.00
G10 L2 P4 X0.00 Y0.00 Z0.00
G10 L2 P5 X0.00 Y0.00 Z0.00
G10 L2 P6 X0.00 Y0.00 Z0.00
G10 L2 P7 X0.00 Y0.00 Z0.00
G10 L2 P8 X0.00 Y0.00 Z0.00
G10 L2 P9 X0.00 Y0.00 Z0.00
G54
M106 S0.00
M116
G92 E12.78310
M82
M23 "0:/gcodes/bloccaggio-a-pressione-definitivo-v2.gcode"
M26 S13452 P1.015 X118.520 Y115.714
G0 F6000 Z2.650
G0 F6000 X128.952 Y115.714
G0 F6000 Z0.650
G1 F450.0 P0
G21
M24 -
@3dream, I confirm that this is a bug. Bed and chamber heat on/off and temperature settings are not written to resurrect.g.
-
@dc42
Good morning,
Thanks for the reply
The temperature of the extruder and chamber are recorded.
is there any way around this?
I would prefer that the chamber does not turn on again or at least that the machine does not wait to reach its temperature before starting.
While the bed would need to be registered. -
@3dream, why would you not want to restore chamber heat before the print is resurrected?
The workaround is that before you resurrect a print, manually set the bed temperature to the required value.
-
@dc42 because the chamber temperature is also reached thanks to the bed. If I forget to activate the bed before pressing resume I cannot activate it again until I reach the chamber temperature. However, it takes a long time to reach the chamber temperature if it has been left very high.
Instead of waiting for the chamber target it could activate but not wait to reach it (like M104).
When do you think you can close this hole? I would really appreciate it
Thank you -
@3Dream, you could turn off the chamber heat in resurrect-prologue.g before the M116 command. Or you could leave it on, but use a more selective M116 command that doesn't wait for the chamber temperature.
-
I've found the bug that was causing the bed heater state not to be written to resurrect.g when there was also a chamber heater. The fix will be in firmware 3.3beta3.
-
@dc42 , Ok, but first the resurrection is read where M141 starts for the chamber and only then is the right prologue read? Therefore it would still wait for the chamber temperature before advancing. Or am I wrong?
-
@3dream, M141 does not wait for temperature to be reached.
-
@dc42 Thank you
It worked for the chamber