stalling and destroying stepper drivers
How long have you been using 8 microsteps?
Have you tried using 16 interpolated all around?
@phaedrux I went to 8 microsteps only recently when I started to get the random stalling problem that I identified earlier. Is there a reason I should go to 16 over 8? I am using the duet as a controller for a pick and place machine for little boxes so I don't need much precision.
Could I have sized my motors incorrectly? I used this guide but I am not sure where any of the equations are derived from. @dc42 could you shed some light?
16 microsteps interpolated to 256 will give the smoothest and quietest operation. I'm not sure if using 8 would have any negative effects in your case but there have been times where full stepping can have issues.
If you move the carriages by hand with the power off and motors disconnected do they move smoothly? It sounds like you have some binding issues still.
@phaedrux Interesting. Everything moves beautifully now by hand with the belts and motors and without the belts and motors attached.
A good example is yesterday I had the problem I described and 45 minutes into my operation the y axis stalled. I swapped out the board and then I went problem free for 10 hours....I which I knew the source of this problem but currently I can only think that the drivers are the source. My rails have 3 rollers on them and I can test them at 80,000mm/min with no issues but going through long procedures I used to get stalling (until I swapped the board). I'm mostly just trying to find root cause for the problem.
@injoi9000 said in stalling and destroying stepper drivers:
M906 X1600 Y2000 Z0 U0 ; Set motor currents (mA)
You say in your first post you have 2A motors? and it looks like you are using the Y motor at max current? That may be your issue. Is the motor getting very hot? Do you have the board actively cooled with a fan blowing over both sides? Try reducing your Y motor current to 70-85% of max rated current.
@phaedrux Yup I have 2A motors. My motors only get warm to the touch and I have them mounted to an aluminum block for heat sinking. I have a 80mm 30cfm fan and I have position the duet as a blade in the middle of the fan so i get airflow on top and bottom.
What is the problem with having my motors at 100% max current? That is their rated current right?
@phaedrux So I have read that portion, however, I have several machines run perfectly fine at 100% of rated current and none of my motors get hot. That also doesn't explain how I can pop in a new duet and fix the stalling issues....seems odd.
Just throwing ideas out there. I would try running at 16 microsteps interpolated at 85% rated current and seeing how that goes. If it still occurs, send M122 to get a diagnostic report and post that here, perhaps that will give another clue.
@phaedrux Hmm ok I will try that. Thanks for the ideas....it is a tricky problem! Do you have any literature on the effects of running motors at rated current with proper heat sinking?
@injoi9000 yeah there was actually a discussion about doing exactly that recently.
Here you go.
https://forum.duet3d.com/topic/6797/setting-motor-current-higher-than-rated-current
Do you happen to have an IR thermometer to check the actual motor temps?
For my own 2.0A motors, I know they can get up to 80c if I run them at full current after several hours on a long high speed print. I don't think I was getting any missed steps and there was no stalling. I've added some heatsinking and run at 70% current and the temps are down to 42c. Same performance and a bit quieter.
I'm not exactly sure what your exact application is, or what your mechanics look like, so it's hard to know what else to try. The fact that the problem goes away when you swap the board leads me to wonder what a diagnostic report would say.
Also, which firmware version are you using exactly? Have you checked the recent upgrade notes to see if there have been any bug fixes or changes that might be relevant?
Ok so I have an update! I just transported my machine 400 miles to a friends house in a uhaul truck and in the first operation the motors stalled. This was after the machine was working continuously For 30 hours! I will run diagnostics on this board but I have a feeling once I swap out the duet everything will work again.....how sensitive is the duet to static electricity or shock/vibration similar to something that might occur during transport?
I looked at one of the old boards and took a diagnostic of it. Not sure what to look for but here it is.
RepRapFirmware for Duet 2 WiFi/Ethernet version 2.01(RTOS) running on Duet WiFi 1.02 or later
Board ID: 08DGM-956GU-DJMSN-6J1FJ-3S06M-K9QRH
Used output buffers: 1 of 20 (1 max)
Static ram: 28476
Dynamic ram: 95768 of which 0 recycled
Exception stack ram used: 204
Never used ram: 6624
Tasks: NETWORK(ready,1872) HEAT(blocked,1256) MAIN(running,4488)
Owned mutexes:
Last reset 00:01:40 ago, cause: power up
Last software reset at 2018-09-25 13:02, reason: User, spinning module GCodes, available RAM 6364 bytes (slot 2)
Software reset code 0x0003 HFSR 0x00000000 CFSR 0x00000000 ICSR 0x0041f000 BFAR 0xe000ed38 SP 0xffffffff Task 0x4e49414d
Error status: 0
[ERROR] Error status: 0Free file entries: 10
SD card 0 not detected, interface speed: 30.0MBytes/sec
MCU temperature: min 40.9, current 43.6, max 43.6
Supply voltage: min 0.6, current 1.7, max 1.7, under voltage events: 0, over voltage events: 0
Driver 0: ok, SG min/max not available
Driver 1: ok, SG min/max not available
Driver 2: ok, SG min/max not available
Driver 3: ok, SG min/max not available
Driver 4: ok, SG min/max not available
Slowest loop: 0.16ms; fastest: 0.07ms
Hiccups: 0, StepErrors: 0, LaErrors: 0, FreeDm: 240, MinFreeDm: 240, MaxWait: 0ms, Underruns: 0, 0
Bed compensation in use: none
Segments left: 0
Stack records: 0 allocated, 0 in use
Movement lock held by null
http is idle in state(s) 0
telnet is idle in state(s) 0
file is idle in state(s) 0
serial is ready with "M122" in state(s) 0
aux is idle in state(s) 0
daemon is idle in state(s) 0
queue is idle in state(s) 0
Code queue is empty.
=== Network ===
Slowest loop: 0.16ms; fastest: 0.01ms
HTTP sessions: 0 of 8- WiFi -
Network state is disabled
WiFi module is disabled
Failed messages: pending 2779096485, notready 2779096485, noresp 2779096485
=== Expansion ===
- WiFi -
Was this after a failure?
@phaedrux This was many power cycles after a failure. Should I send the command immediately after a failure?
It could also be wiring problem. When you swap the board around the connectors and cables get moved around and they are working again. Have you tried to wiggle the connectors and cables when the gantry is moving to see if that has any effect?
I've also had some random stalling problems after assembling my machine and they turned out to be my bad crimp connections.
Yes. Any error message is reset at a power cycle.
- Can you post a photo of your Duet cooling setup?
- Do you ever see temperature warning messages on the GCode Console page of DWC?
- Which firmware version are you using?
- Picture below
*I have never seen a temperature warning
*I am using firmware version 2.00
*Here is an diagnostic message I received after one of these random stalls:
RepRapFirmware for Duet 2 WiFi/Ethernet version 2.0(RTOS) running on Duet WiFi 1.02 or later
Board ID: 08DGM-9T6BU-FG3SN-6JKD2-3S46S-1UYHF
Used output buffers: 2 of 20 (7 max)
Static ram: 28380
Dynamic ram: 95476 of which 0 recycled
Exception stack ram used: 452
Never used ram: 6764
Task NETWORK ready, free stack 324
Task HEAT blocked, free stack 1256
Task MAIN running, free stack 3876
Last reset 02:24:17 ago, cause: power up
Last software reset details not available
Error status: 0
SD card longest block write time: 60.5ms
MCU temperature: min 13.7, current 21.2, max 24.0
Supply voltage: min 13.8, current 24.1, max 24.4, under voltage events: 0, over voltage events: 0
Driver 0: standstill, SG min/max 0/1023
Driver 1: standstill, SG min/max 0/1023
Driver 2: standstill, SG min/max 0/1023
Date/time: 2018-09-28 14:54:25
Slowest loop: 40.42ms; fastest: 0.07ms
Hiccups: 0, StepErrors: 0, LaErrors: 0, FreeDm: 240, MinFreeDm 234, MaxWait: 2388690272ms, Underruns: 0, 0
Scheduled moves: 2628, completed moves: 2628
Bed heaters = -1 -1 -1 -1, chamberHeaters = -1 -1
Segments left: 0
serial is idle in state(s) 0
=== Network ===
Slowest loop: 70.18ms; fastest: 0.01ms
HTTP sessions: 1 of 8
- WiFi -
Network state is running
WiFi firmware version 1.21
WiFi MAC address 84:f3:eb:83:35:c6
WiFi Vcc 3.44, reset reason Turned on by main processor
WiFi flash size 4194304, free heap 14864
WiFi IP address 192.168.1.2
WiFi signal strength -45dBm, reconnections 0, sleep mode modem
=== Expansion ===
- Picture below
@injoi9000 Just looking at that M122......
So at some point, the supply voltage dropped from around 24v to 13.8v. Just wondering if that is the root cause of the problem - perhaps a dodgy power supply?
