RRF Config Mapping
-
@Phaedrux Ok thanks.
-
Now I'm stuck with error at bed heating.
Error: Heater 0 fault: temperature rising much more slowly than the expected 1.7°C/sec
Duet 2 Wifi power a solid state relay for a 220v heater.I executed M307 H0 S90
M307 H0 results in below.
Heater 0 model: gain 340.0, time constant 140.0, dead time 5.5, max PWM 1.00, calibration voltage 0.0, mode bang-bangThen I tried to save the value
M307 H0 A340 C140 D5.5 V0 B0
But it result in
Warning: M307: Heater 0 appears to be over-powered. If left on at full power, its temperature is predicted to reach 365C -
That's expected. The warning is letting you know what the max uncontrolled temp could be.
-
@Phaedrux Ok, but I still not able to heat the bed. It start heating but halt after few seconds. Error: Heater 0 fault: temperature rising much more slowly than the expected 1.7°C/sec
-
Are you sure you saved the PID tuning results with M500? Do you also have an M501 at the end of config.g to load the saved results?
-
@Phaedrux i was missing M501 in config.g
Restarted boad but getting same error when trying to heat bed.
Tried to run M307 H0 S90 again but it fails with Error: M307: bad model parameters; config-override.g file generated in response to M500 at 2020-07-10 23:02 ; This is a system-generated file - do not edit ; Heater model parameters M307 H0 A340.0 C140.0 D5.5 S1.00 V0.0 B1 M307 H1 A340.0 C140.0 D5.5 S1.00 V0.0 B0 ; Workplace coordinates G10 L2 P1 X0.00 Y0.00 Z0.00 G10 L2 P2 X0.00 Y0.00 Z0.00 G10 L2 P3 X0.00 Y0.00 Z0.00 G10 L2 P4 X0.00 Y0.00 Z0.00 G10 L2 P5 X0.00 Y0.00 Z0.00 G10 L2 P6 X0.00 Y0.00 Z0.00 G10 L2 P7 X0.00 Y0.00 Z0.00 G10 L2 P8 X0.00 Y0.00 Z0.00 G10 L2 P9 X0.00 Y0.00 Z0.00
-
In config.g change M307 H0 B1 S1.00 to B0
Then delete your config-override.g and run M307 H0 S90 again after a reboot. Then save with M500.
-
Also make sure you're starting from a cold bed state.
-
@Phaedrux said in RRF Config Mapping:
Executed M307 H0 S90 after the suggested changes.
Error: M307: bad model parametersUpdate:
My bad, it might be M303 H0 S90 -
-
@Phaedrux said in RRF Config Mapping:
@printthatthing said in RRF Config Mapping:
Update:
My bad, it might be M303 H0 S90Yes of course.
Now it works fine:) Thank you so much for all support.